New guy with my first question. I looked around online for a few hours but couldn't find an answer.
I am currently building my well system for a new house. My pitless adapter will be at 30 inches depth, frost depth here in the Ca high desert. I would like to put a CSV at the outlet of the pitless, rather than hanging it inside the well. Is there a CSV that can be buried directly in the dirt or will it need to be inside some sort of a box? I like the idea of being able to access it easily and dislike having anything extra in the well that could break/unscrew/fail etc.
Thanks in advance for any advice, and thank you for providing this forum so beginners like me can potentially figure things out! :o
Steve
-
Hi Steve
You can't just bury a CSV as it needs to breath a little air to work properly. But you can put it in a valve box or culvert pipe. However, It would probably be easier to access hanging in the well than at the bottom of a 30" deep valve box, but a lot of people do it that way. The CSV125 is made to hang in the well as long as you don't have more than 500# of weight on it.
-
Hi Cary,
Thanks for the reply. I'll have to think about what I want to do. Have you heard of anyone having problems putting the CSV in the well and having it break off or unscrew from the pump starting torque? I probably won't have much more than 100 pounds hanging on it.
Thanks again,
Steve
-
Been hanging CSV's in the well for 25 years no problem. It takes about 5000# to break a CSV125, so we only recommend 500# or less. Just don't use any pipe dope as that attacks the plastic. Other than that they are as strong as steel.
-
So no pipe dope, but teflon tape is ok?
-
Yes and you can get them as tight as needed, won't come unscrewed. Just no pipe dope.
-
Ok, that's what I will do. Thanks for making the install easier!