Pumps, Wells, Tanks, Controls / Re: Formula for pump math?
« on: September 19, 2023, 04:55:35 PM »
I think maybe my last description wasnt very good lol! I took a video of my pressure gauge with my sink running to show what im talking about but i cant find a way to upload the video here. But it kicks in at 40, pump runs two seconds and kicks out at 60. Pressure drops as faucet runs, 5 seconds to get down to 40 then kicks pump in, 2 seconds and system is back to 60, kicks out. Process repeats. Same with toilet flushes. Keeps doing that until the toilet tank is refilled, hence the 3 or 4 cycles.
I am thinking you were correct the first time about the pressure tank being bad. Doesnt seem to be tripping the pump overload. Its only a 7 gallon tank, but it also could be bad. It has been here the 7 years I have lived here and the system has always acted this way.
And yes, you're right, i forgot about the 1 psi per 2.31ft. Not a good idea to put the CSV right in the pump 50ft down. I will purchase one and put it below the pitless. Thank you for your time and for allowing me to ask my questions here! This is an amazing forum that i have learned a lot from already!
I am thinking you were correct the first time about the pressure tank being bad. Doesnt seem to be tripping the pump overload. Its only a 7 gallon tank, but it also could be bad. It has been here the 7 years I have lived here and the system has always acted this way.
And yes, you're right, i forgot about the 1 psi per 2.31ft. Not a good idea to put the CSV right in the pump 50ft down. I will purchase one and put it below the pitless. Thank you for your time and for allowing me to ask my questions here! This is an amazing forum that i have learned a lot from already!