Recent Posts

Pages: 1 [2] 3 4 ... 10
11
Irrigation / Re: Large Irrigation system
« Last post by Cary Austin on January 02, 2024, 09:11:22 AM »
With a 60/80 pressure switch setting the CSV can be set to maintain 70 PSI constant.  That decreases the differential pressure to about 125 PSI, which is perfect for the CSV1A.
12
Irrigation / Re: Large Irrigation system
« Last post by EPStutes on January 02, 2024, 08:11:08 AM »
Thanks for the quick response. 

I was planning to set the stop pressure to 80psi which is the recommended max operating pressure of the sprinkler control valves.
13
Irrigation / Re: Large Irrigation system
« Last post by Cary Austin on December 31, 2023, 11:09:54 AM »
Looks correct. So, even with a 50' water level and a back pressure of 195 PSI, setting the CSV for 50 PSI leaves 145 PSI differential pressure.  150 PSI is max differential we recommend for the CSV1A, so setting it higher decreases the differential and gives you more pressure at the sprinklers.
14
Irrigation / Re: Large Irrigation system
« Last post by EPStutes on December 31, 2023, 08:03:15 AM »
Cary,

Good morning.  I am also in the process of setting up a large sprinkler system.

My zones rates will range from 10gpm to 28 gpm assuming a 50-75 psi output pressure from the CSV

Pump is a Franklin 25JS3S4-PE and the pump and topsides rate/pressures are shown in the attached table.

The well company installed a CSV1A with a 20gal tank.  Am I figuring the CSV output pressures as shown in my table correctly?  Is this the best setup for my application?

Thanks,

Eric Stutes

15
Frequently Asked Questions / Re: System overhaul recommendations/advice
« Last post by Cary Austin on November 06, 2023, 12:52:56 PM »
The highest pressure shallow well jet pump I know of is the J15S, which will build 83 PSI max and work with a 50/70 switch and a CSV setting of 65 PSI.  https://www.lockewell.com/index.php?main_page=product_info&cPath=1_3_155_92&products_id=549

To get up to 60/80 with the CSV set for 70-75 PSI you will need a multi-stage centrifugal or a submersible.  Here is a multi-stage.  https://www.lockewell.com/index.php?main_page=product_info&cPath=1_3_86&products_id=1743

If you drop in a submersible you can use a pump like this for a fraction of the price.  https://www.ebay.com/p/18030648622

Any of them will work with CSV or the PK1A kit.  But to go 50/70 pressure or higher I would recommend the heavy duty pressure switch and the 10 gallon size tank.  Even with the heavy duty switch you can still turn it down as low as 30/50 if needed.   https://cyclestopvalves.com/pages/pk1a-pside-kick
16
Frequently Asked Questions / Re: System overhaul recommendations/advice
« Last post by Rollaknot on November 06, 2023, 09:45:02 AM »
Thank you Carey for sharing all of your priceless knowledge.  What pump would you recommend for this set up and would it be possible to go ahead and add the PK1A PSIDE-KICK with the 70 psi 60/80 switch and set it to accommodate the existing pump in preparation of upgrading to a bigger pump in the near future?  I am wanting to utilise the irrigation lines that were hear from the previous owners but with the current pressures it struggles.  I suspect they originally had a bigger pump to accommodate prior to the one installed now because they quit using the irrigation.
17
Frequently Asked Questions / Re: System overhaul recommendations/advice
« Last post by Cary Austin on November 04, 2023, 12:17:18 PM »
That pump builds a max pressure of 67 PSI.  That means the highest you can run the pressure switch is about 35/55 with the CSV set for a constant 45 PSI.  The constant 45 from the CSV will make it seem much stronger than when cycling on at 35 and off at 55. 

There must be a check valve.  It is probably on the suction line to the storage tank.  Filters cost you pressure.  Don't filter unless you have to.  You can do it.  The PK1A is easy to install.
18
Frequently Asked Questions / System overhaul recommendations/advice
« Last post by Rollaknot on November 03, 2023, 12:38:51 PM »
My current bladder tank is bad so I am in the beginning stages of overhauling my wellhouse. I am by no means versed in this subject but being on a tight budget I am going to tackle this project myself. I just want to make sure there are no tricks of the trade that I am missing.

I have a 1500 gal storage tank with a Myers Shallow Well Jet Pump 28 GPM 1 HP #HJ100S which then feeds the bad pressure tank at the moment.  After the bladder tank I have a 1" tee where one side feeds the house and the other 1" line feeds a irrigation line/hose bib.

My plan is to re-plumb the whole well house and install the PK1A PSIDE-KICK with the 70 psi 60/80 switch.  One question I had is, will the Myers pump build that much pressure?

The current system does not have any check valves of any sort, and we are still debating on whether or not to add inline filters.

Any advice is greatly appreciated.
19
I have seen dramatic increases with steel casing.  PVC not so much.  But the brushing and bailing only cleans up the perforations so what water is there can get in.  If the water isn't there it won't help much.
20
Thanks Cary,
Yes, you did answer this question on another website.
I posted here the morning of Sat. Sept 30 and I posted on the other site that afternoon before you answered here.

I agree with you on 1.25 gpm being considered a dry well. Unfortunately common sense on the left coast is not as common as it is in Texas and the county I live in has an alternate sense of reality.

I will check again with the well drillers to see if there has been any changes, for the better, in my county.

What is the average percent of gpm increase that you have experienced with a brush and bail?


 Would it usually be worth spending $1,000 and removing a new roof from a 12' tall pump house?

Thanks again
Ken
Pages: 1 [2] 3 4 ... 10