110 PSI is nothing. Like you said your pipe is probably rated at 200 PSI, which means the burst pressure should be at least twice that much. Most likely you have too many check valves. A check valve on the pump is the only one needed. If you have another check up top, especially before the pressure tank, the water hammer that happens between those check valves can cause 500 PSI spikes during pump start. A steady 110 or even 200 PSI won't hurt the pipe. But those little spikes between check valves will blow fittings or split the pipe.