Author Topic: Using CSV1's in parallel.  (Read 10220 times)

speedbump

  • Guest
Using CSV1's in parallel.
« on: April 04, 2007, 10:03:17 AM »
Since most jet pumps are tapped 1" on the discharge and a 1, 1.5hp can do in some cases better than 25 gpm, would it be better to use the 1-1/4" valve or use two CSV1's in parallel.  Not only for ease of not bushing up and down and making it look like an abortion.  But for the lack of pressure losses etc?

bob...

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Using CSV1's in parallel.
« Reply #1 on: April 04, 2007, 10:39:24 AM »
The CSV1.25 will basically do the same as two of the CSV1 valves in parallel.  I have had customers who used as many as four of the CSV1 valves in parallel for 100 GPM pumps.  They work great this way as long as you can get them installed without bending them or getting them in a bind.  Manifolding two or more valves together, it is just hard to keep them square or plumb.

speedbump

  • Guest
Using CSV1's in parallel.
« Reply #2 on: April 04, 2007, 11:57:31 AM »
Does the CSV1-1/4" have the same 1 gpm fill rate to the tank as the CSV1?

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Using CSV1's in parallel.
« Reply #3 on: April 04, 2007, 12:08:17 PM »
The CSV1.25 has about a 2.5 GPM minimum.  So if you use two of the CSV1's in parallel, you have about a 2 GPM minimum.  Four in parallel would give you a 4 GPM minimum and so on.

speedbump

  • Guest
Using CSV1's in parallel.
« Reply #4 on: April 04, 2007, 12:39:03 PM »
Ok, gotcha.

That answers that question.  Be prepared for many more.

Thanks,

bob...