Affinity Laws and CSV vs VFD.
« on: April 28, 2015, 09:21:39 PM »
I found this article very helpful in understanding pump curves.

Hope the link and this quote is allowed;

Quote
http://www.pump-magazine.com/pump_magazine/pump_articles/article_44/article_44.htm
Observations:

For friction-dominated systems (long pipes, flow transfer cases) VFD saves a very substantial amount of energy, and operates pumps reliably due to close proximity to BEP flow (100% in example shown)

Tried to fix link, added below.  Cary

Tried to fix link, added below.  Cary
For static-dominated systems (injection against constant pressure, lifting against constant head) the energy savings are substantially less, and the pump operates, surprisingly, substantially off-BEP position, not significantly different from a valved flow control case

For cases where both systems are present, an in-between scenario would result



So, in a average residential single household situation. The $2-$4 (I figured pump on a total of 3 hours a day) you would save in electricity per month would never pay the additional cost of the VFD over the VFD's lifespan.

Hope that helps someone else.
« Last Edit: May 04, 2015, 07:01:18 AM by Cary Austin »

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Re: Affinity Laws and CSV vs VFD.
« Reply #1 on: May 01, 2015, 08:50:20 AM »
Thanks ByteMe.  Here are a couple more examples from a few others who understand a VFD cannot save energy with most pumping applications.


http://www.pump-magazine.com/pump_magazine/pump_articles/article_44/article_44.htm

For static-dominated systems (injection against constant pressure, lifting against constant head) the energy savings are substantially less, and the pump operates, surprisingly, substantially off-BEP position, not significantly different from a valved flow control case.



http://files.engineering.com/download.aspx?folder=c3f30ccc-8fd9-412f-a269-0379249f4bea&file=20100212_VFD.ppt

—Invest in the mechanical engineering and specify correctly
—VFDs do not always save energy,
—VFDs provide a suitable solution to some pump operating conditions but should not be considered a panacea
—“You just can't ever beat the energy efficiency of running a properly sized pump at 100% BEP rated flow”.
—Mechanical engineers have a poor understanding of electric motors & VFDs and fail to communicate with process or electrical engineers





http://www.powerqualityanddrives.com/payback_analysis_vfd/

Since the affinity curve neglects the static head of the system as seen
by the pump, most applications will save between 1/2 and 1/3 of what is
determined by the affinity curve calculation.




http://www.cyclestopvalves.com/pdf/csv-vs-vfd_16.pdf

When backpressure increases to a certain level, the power drawn by the variable speed control condition is very close to that for a throttle valve.

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Re: Affinity Laws and CSV vs VFD.
« Reply #2 on: May 04, 2015, 06:56:05 AM »
http://www.pump-magazine.com/pump_magazine/pump_articles/article_44/article_44.htm

For static-dominated systems (injection against constant pressure, lifting against constant head) the energy savings are substantially less, and the pump operates, surprisingly, substantially off-BEP position, not significantly different from a valved flow control case.


I don't know why this link would not work on your first post, so I just added it again here.
« Last Edit: May 04, 2015, 06:58:29 AM by Cary Austin »