Hi Ron, thought I might chime in. Very good explanation of how a CSV stops water hammer. I have learned something recently. You do not have to have the CSV set at the same pressure as the pressure switch ON setting to eliminate water hammer. With a 60/80 pressure switch you could set the CSV for 70 PSI and the pump will still start at 5 GPM with no water hammer. It seems that even though the CSV is set at 70 and the pump starts at 60, the CSV will still be in the closed to 5 GPM position when the pump starts. It will not stay in this position for long but, will still absorb the shock wave as the pump starts, then quickly opens to allow full flow from the pump until pressure reaches 70 PSI. The loading chamber or bonnet of the CSV will be full of water holding the valve closed when the pump starts. As soon as the pump starts, the flow from the pump will begin to lift the diaphragm to an open position. The diaphragm will still only open as fast as the water in the diaphragm chamber can be pushed out through the pilot valve and control tubing. In other words, with the valve set at 70 using a 60/80 pressure switch, the valve will quickly open when the pump starts but, will still make the pump start at 5 GPM which eliminates water on pump start up. The CSV must still be set lower than the OFF setting of the pressure switch to eliminate water hammer during pump shut off and also to allow the CSV to function.