I installed the CSV1W in an above ground application (was told it could be used either in the well or above ground). The valve is immediately before a water filter which is immediately prior to the pressure switch and tank.
The on/off for the pump is 40/60psi and the valve is at 50psi. I confirmed the CSV 50PSI by running water in the mechanical room and observing at which point the valve holds the pressure (I lowered it from the factory preset of 60psi).
When one faucet or bathtub faucet is opened 100%, the valve believes its getting less than 1GPM and, therefore, lets the pump build pressure and shuts off at 60psi. However, I gotta believe a bathtub faucet (not the showerhead) is putting out more than 1GPM. If I crack open the faucet in the mechanical room while letting the bathtub faucet run open 100%, this provides enough water flow for the CSV to maintain 50psi and not allow the pump to cycle.
I guess what I'm saying with all this is if the CSV won't stop the pump from cycling when only one faucet is open 100% in a household application, the value of the CSV is greatly diminished.
Or did I install something incorrectly?! Which may be the more appropriate question!
thanks, John