Author Topic: Can PK1A take the place of the AV22 kit for a Goulds J5 pump?  (Read 5313 times)

Josh L.

  • Newbie
  • *
  • Posts: 1
    • View Profile
I am going to be replacing a double drop (deep well) jet pump and a 36 gallon pressure tank in the near future. I want to use a Goulds J5 pump (the closest thing to the Goulds pump now in use) and I want to replace the pressure tank with a PK1A to save space, and hopefully stabalize water pressure in the house. My question is, can I forego the AV22 kit the Goulds J5 pump says is required since the PK1A already has a pressure control valve?

"•Deep well systems require a pressure control valve.
?NOTE: YOU MUST HAVE A JDW OR AV22 KIT TO MAKE THE PRESSURE SWITCH CONNECTION.
•Pressure tank required on all systems."

Thanks for any advice!

Josh L.

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1586
    • View Profile
    • http://www.cyclestopvalves.com
Re: Can PK1A take the place of the AV22 kit for a Goulds J5 pump?
« Reply #1 on: June 02, 2012, 05:40:15 PM »
Yes you still need the back pressure valve for a two pipe jet pump.  The CSV controls the output of the pump, and the back pressure valves sends enough water to the ejector to make the two pipe jet work.