Author Topic: Setting CVS1W pressure  (Read 4506 times)

brewman

  • Newbie
  • *
  • Posts: 1
    • View Profile
Setting CVS1W pressure
« on: July 17, 2013, 03:04:22 AM »
Just purchased CSV1W was wondering how to set pressure setting. I'm installing a 2hp 15 gpm pump set at 300ft, static water level 145ft, with 1-1/4" poly up to the CSV1W from there supply line is 1".  I have a sprinkler system with max demand at 16 gpm.  Looking at the pressure fall off chart I should set the valve to 62 psi for running 50 psi. Is this correct? How do I know I'm at that setting before setting the pitless adapter assembly into the well? My pressure tank has a 14 gallon draw down, pressure switch is currently at 40/60.

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Re: Setting CVS1W pressure
« Reply #1 on: July 17, 2013, 07:27:31 AM »
Two full turns to the right will change the setting from 50 to 60 PSI.  Then you will need to turn the pressure switch up to about 45/65 with that size tank.  That will take a bout two full turns to the right on the large adjustment screw in the pressure switch.