Author Topic: Low pressure issues  (Read 1864 times)

jark0218

  • Newbie
  • *
  • Posts: 3
    • View Profile
Low pressure issues
« on: November 14, 2021, 03:30:28 PM »
I currently have a CVS1A setup but am experiencing very low pressure throughout the house.  Basically we can only use one fixture at a time.  I have a 305' well with a Goulds 3/4 hp 7 GPM series pump.  Based on your compatible pump types the maximum depth to water level is 215'.  Could this be the issue?  If so, do you have any suggested solutions.  Thanks

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Re: Low pressure issues
« Reply #1 on: November 14, 2021, 04:00:58 PM »
What pressure is on the gauge?

jark0218

  • Newbie
  • *
  • Posts: 3
    • View Profile
Re: Low pressure issues
« Reply #2 on: November 15, 2021, 06:46:36 AM »
Pressure gauge says 60 psi

Cary Austin

  • Inventor, Owner, Chief Cook and Bottle Washer
  • Administrator
  • Newbie
  • *****
  • Posts: 1599
    • View Profile
    • http://www.cyclestopvalves.com
Re: Low pressure issues
« Reply #3 on: November 16, 2021, 08:28:43 AM »
With 60 PSI you would not even need soap in the shower it would be so strong.  You must have a blockage after the gauge.  Do you have a filter clogged or a valve partially closed?

jark0218

  • Newbie
  • *
  • Posts: 3
    • View Profile
Re: Low pressure issues
« Reply #4 on: November 16, 2021, 06:17:48 PM »
Yes filter was clogged.  Issue solved!  Thanks!